消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

设有门斗的外门能作为自然补风口吗

箭头位置可以作为自然补风口使用吗?

金高银 | 2024-10-29 17:07
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

潘天坤 2024-10-29 17:35 10 [回复]举报

门斗内应该不需要设置防排烟设施,然后如果是室内的补风设施应该是直接通过室内的外墙进行补风(中间存在门斗等区域可能不属于从室外引入空气)

防火门、窗不得用作补风设施,普通疏散门一般没有限制,不过可能要考虑门斗处设置是否合理(门斗可能设置在有爆炸危险的区域)


LHH2737 2024-10-30 09:31 10 [回复]举报

不可以,补风口应设置在某一防烟分区内,门斗区域不属于任何一个防烟分区

防排烟规范第4.5.4条文解释:补风口可设置在本防烟分区内,也可设置在其他防烟分区内。

关闭

关闭

手机APP下载