消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

建筑防火通用规范中8.1.9中9设置在多层建筑第一层至第三层且楼层建筑面积大于300平米,这300平米是指总面积还是每层面积呢?

通用规范中8.1.9中9设置在多层建筑第一层至第三层且楼层建筑面积大于300平米,这300平米是指总面积还是每层面积呢?

淡定119 | 2024-07-08 08:36
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

周家斌 2024-07-08 09:04 00 [回复]举报

参考石老师《解读与应用》

消防检查 2024-07-08 09:08 00 [回复]举报

个人理解是每层的建筑面积。8.1.9里,涉及总面积的都表述为总建筑面积,而“多层建筑第一层至第三层且楼层建筑面积大于300平米”,提出的是“楼层”建筑面积。

香.香 2024-07-08 09:14 00 [回复]举报

任一层大300要设,总的大300要设

无名之辈 2024-07-08 09:23 10 [回复]举报

300㎡指的是歌舞娱乐场所每层的建筑面积,不是总面积,也不是自然层的建筑面积,通规实施指南有相关说明。

消防网友68723 2024-07-08 09:44 10 [回复]举报

楼层建筑面积大于300平米

LHH2737 2024-07-08 09:44 10 [回复]举报

整个建筑每层的面积

潘天坤 2024-07-08 09:58 10 [回复]举报

从正文和条文说明的文字来看,没有区分是每层还是总建筑面积,不过按照原建筑设计防火规范GB50016原文和建筑防火通用规范 GB55037-2022配套的实施指南,可能理解为每层建筑面积。不过配套实施指南的效力是小于规范正文的,只能辅助理解,具体需要看地区内设计、审查、专家们怎么认定

上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

建筑防火通用规范 GB55037-2022配套的实施指南有提到:

第8.1.9条第9款规定的歌舞娱乐放映游艺场所, 包括独立建造的歌舞娱乐放映游艺场所、设置在其他建筑内的歌舞娱乐放映游艺场所:
1)设置在地下、半地下的歌舞娱乐放映游艺场所,无论场所的建筑面积大小, 均应设置自动灭火系统;
2)设置在多层建筑的地上第四层及以上楼层的歌舞娱乐放映游艺场所,无论场所的建筑面积大小,均应设置自动灭火系统;
3)设置在高层民用建筑内的歌舞娱乐放映游艺场所,无论场所的建筑面积大小,均应设置自动灭火系统;
4)设置在单层建筑内的歌舞娱乐放映游艺场所,当该场所建筑面积大于300平方米时,应设置自动灭火系统;
5)设置在多层建筑的第一层至第三层的歌舞娱乐放映游艺场所,当歌舞娱乐放映游艺场所的每层建筑面积大于300平方米时,应设置自动灭火系统。 本款的多层建筑包括单层建筑

笨笨1 2024-07-08 11:21 00 [回复]举报

建筑面积大于300平方米的前面你看一下他的定于表述,当任一楼层的歌舞娱乐场所的建筑面积大于300平方米。所以我的理解就是这个多层建筑就是楼层面积有500平方米,只要本层歌舞娱乐场所不超过300平方米,就可以不用设置自动喷水设施

消防网友346 2024-07-09 09:32 00 [回复]举报

这里指每一层的面积均大于300㎡要设置的。


关闭

关闭

手机APP下载