关于栓规3.5.3怎么理解

3.5.3 当建筑物室内设有自动喷水灭火系统、水喷雾灭火系统、泡沫灭火系统或固定消防炮灭火系统等一种及以上自动水灭火系统全保护时,高层建筑当高度不超过50m且室内消火栓系统设计流量超过20L/s时,其室内消火栓设计流量可按本规范表3.5.2减少5L/s;多层建筑室内消火栓设计流量可减少50%,但不应小于10L/s。


如果一个小区,多层商业设置喷淋,消火栓流量25L/s。减少50%为12.5L/s。地库流量10L/s,住宅流量10L/s。那地库消火栓环状管网是否可以采用DN100?商业、住宅、地库全部从环状管网接支管。

小学生123 | 2024-06-07 10:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

jinyanwu 2024-12-04 14:59 00 [回复]举报

这个喷淋有个定义是“全保护”;这个条件一定要满足。

流量和管径不是直接的对应关系,还要考虑管网压力和损失因素。但根据目前常用的使用压力,大致应该够用了。