消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水炮能否和自喷系统共用水泵(在流量和扬程都满足的情况下),是否需要设置单独的水炮泵?

消防水炮能否和自喷系统共用水泵(在流量和扬程都满足的情况下),是否需要设置单独的水炮泵?

WeiHL | 2024-04-18 14:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

安洪全 2024-04-18 16:31 10 [回复]举报


灭火英雄 2024-04-18 17:02 00 [回复]举报

废话,那肯定的,这是两个系统怎么可以共用水泵,规范里面明令禁止你还问这种问题

CN88 2024-04-18 17:31 20 [回复]举报

根据《自动跟踪定位射流灭火系统技术标准 GB51427-2021》

4.5.2 自动消防炮灭火系统应设置独立的消防水泵和供水管网,喷射型自动射流灭火系统和喷洒型自动射流灭火系统宜设置独立的消防水泵和供水管网。

4.5.3 当喷射型自动射流灭火系统或喷洒型自动射流灭火系统与自动喷水灭火系统共用消防水泵及供水管网时,应符合下列规定:    

1 两个系统同时工作时,系统设计水量、水压及一次灭火用水量应满足两个系统同时使用的要求;    

2 两个系统不同时工作时,系统设计水量、水压及一次灭火用水量应满足较大一个系统使用的要求;    

3 两个系统应能正常运行,互不影响。



喷射型自动射流灭火系统和喷洒型自动射流灭火系统可与自动喷水灭火系统共用消防水泵及供水管网。


喷射型自动射流灭火系统:灭火装置的流量不大于16L/s且不小于5L/s、射流方式为喷射型的自动跟踪定位射流灭火系统。

喷洒型自动射流灭火系统:灭火装置的流量不大于16L/s且不小于5L/s、射流方式为喷洒型的自动跟踪定位射流灭火系统。


南明离火 2024-04-19 09:55 00 [回复]举报

可以,报警阀前共用

关闭

关闭

手机APP下载