消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

应急灯接线标准规范

应急灯接线要求直接接电源线,不得使用插头接电源的标准依据是什么?

akon | 2021-02-03 17:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

阳光哥哥 2021-02-04 21:58 00 [回复]举报

使用插头随意性太大,如与突发紧急情况如插头被人拔掉会影响逃生救援!国家标准已禁止使用插头连接,请按国家标准执行!

消防网友75620 2021-02-05 15:34 00 [回复]举报

消防应急照明和疏散指示系统技术标准 GB51309-2018 > 4.4.3 应急照明控制器主电源应设置明显的永久性标识,并应直接与消防电源连接,严禁使用电源插头;应急照明控制器与其外接备用电源之间应直接连接。

小马 2021-03-04 09:21 00 [回复]举报

使用插头的话,我看有些场所把指示牌的插头拔掉,插头挪作他用。。

横行霸道的螃蟹 2021-11-02 23:34 00 [回复]举报

4.5.5 非集中控制型系统中,自带电源型灯具采用插头连接时,应采用专用工具方可拆卸。


条文解释

4.5.5 采用自带电源型灯具的非集中控制型系统中,灯具可以采用插头方式连接;但是,为了避免在日常使用过程中非维护人员随意拔出插头,影响灯具的正常运行,插头与插座之间应采取采用专用工具方可拆卸的连接方式连接。


说明其他几种形式不能用插头了,而且用插头的这种形式还得符合条文解释中所要求的方法连接。

周家斌 2022-05-10 11:48 00 [回复]举报

采用自带电源型灯具的非集中控制型系统中,灯具可以采用插头方式连接;但是,为了避免在日常使用过程中非维护人员随意拔出插头,影响灯具的正常运行,插头与插座之间应采取采用专用工具方可拆卸的连接方式连接。

关闭

关闭

手机APP下载