造纸厂要设喷淋吗

一栋四层丁类厂房,总建筑面积三千五百平方米,二楼设置了的造纸厂要设自喷和报警系统吗

六六大顺 | 2024-01-25 19:50
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

BOLIN 2024-01-26 09:52 20 [回复]举报

8.3.1 除本规范另有规定和不宜用水保护或灭火的场所外,下列厂房或生产部位应设置自动灭火系统,并宜采用自动喷水灭火系统:
    1 不小于50000纱锭的棉纺厂的开包、清花车间,不小于5000锭的麻纺厂的分级、梳麻车间,火柴厂的烤梗、筛选部位;
    2 占地面积大于1500m²或总建筑面积大于3000m²的单、多层制鞋、制衣、玩具及电子等类似生产的厂房;
    3 占地面积大于1500m²的木器厂房;
    4 泡沫塑料厂的预发、成型、切片、压花部位;
    5 高层乙、丙类厂房;
    6 建筑面积大于500m²的地下或半地下丙类厂房

3.1.2 同一座厂房或厂房的任一防火分区内有不同火灾危险性生产时,厂房或防火分区内的生产火灾危险性类别应按火灾危险性较大的部分确定
你这属于 丙类厂房吧,和第二条类似应该设吧

马先生 2024-02-24 12:03 00 [回复]举报

1、丁类厂房;如有相关备案文件确定丁类厂房,不需要设置自喷及报警系统。只需要设置消火栓。

2、二楼设置造纸厂;因改变使用性质及用途,应当重新向有关部门重新申请消防备案验收;造纸厂属于丙类,应依据使用面积(占地1500m²或总面积超过3000m²)设置自喷及报警系统。

3、二楼设置造纸厂;造纸厂单独设置自喷及自动报警系统。