消防喷淋泵和消防水池是必须得吗?

实际改造过程中发现很多既有建筑是需要增设喷淋系统的,但实际情况,增设水泵房和消防水池是无法实施的,请问,什么情况下喷淋系统可以不设置喷淋泵和消防水池?万分感谢!

消防杜 | 2023-07-24 11:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

周家斌 2023-07-24 11:53 10 [回复]举报

可以了解一下局部应用系统

安洪全 2023-07-24 13:29 00 [回复]举报

可以了解一下“一体化预制泵站工程技术标准CJJ/T285-2018”


北京市既有建筑改造工程消防设计指南(2023年版)

4.1.8 现状无消防水池及消防水泵房的建筑局部改造工程,因改造需增设消火栓、自动喷水灭火等系统但增设消防水池、消防水泵房确有困难时,可采用符合现行消防技术标准的一体化消防给水泵站替代。

【说明】建筑局部改造工程,因无法增加建筑面积,在原室内空间增设水池、水泵房极困难。室外埋地安装的一体化消防给水泵站占地小,施工安装较便利,可以解决上述问题。

同同不同 2023-07-24 13:50 10 [回复]举报

如市政消防水满足要求或高位消防水池,可采用高压消防给水