酒店大堂是否需要满足疏散门数量不应少于2个的要求?

酒店大堂是否需要满足疏散门数量不应少于2个的要求?

Madapple | 2023-04-12 09:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

虎斑贝 2023-04-12 16:59 00 [回复]举报

正常都需要,具体详见建筑设计防火规范 GB50016-2014(2018年版)5.5 安全疏散和避难,Ⅱ 公共建筑部分

5.5.8 公共建筑内每个防火分区或一个防火分区的每个楼层,其安全出口的数量应经计算确定,且不应少于2个。设置1个安全出口或1部疏散楼梯的公共建筑应符合下列条件之一:     

1 除托儿所、幼儿园外,建筑面积不大于 200m² 且人数不超过50人的单层公共建筑或多层公共建筑的首层;     

2 除医疗建筑,老年人照料设施,托儿所、幼儿园的儿童用房,儿童游乐厅等儿童活动场所和歌舞娱乐放映游艺场所等外,符合表5.5.8规定的公共建筑。