水喷雾系统需要设消防水箱吗?

一光伏升压站,设室外消防给水系统及变压器水喷雾系统,合用临时高压给水系统。《喷规》要求设消防水箱,《水喷雾》没有要求,问需要设高位消防水箱吗?

举人 | 2022-10-04 15:41
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

风往南吹 2022-10-06 11:23 00 [回复]举报

你这个问题不在于《喷规》要求设消防水箱,《水喷雾》没有要求。而是在于系统组件的问题与工作原理。水喷雾系统就是一个开式系统,阀门开,水泵开就有水,系统要求的有响应时间。该系统不存在什么高位水箱

消防黄河 2022-10-06 23:19 00 [回复]举报

您所描述不是很清楚。水喷雾和室外栓合用水泵?两者工作压力要求差距较大,一般不合用。若合用,为保证室外栓供水压力,应设高位水箱。单水喷雾系统,不需要高位水箱。

周家斌 2022-10-07 12:49 00 [回复]举报