消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于大厅室疏散距离

图2中b1+b2≤45m,这个计算值是怎样得来的?


永锅 | 2022-09-21 08:48
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防网友68723 2022-09-21 09:20 00 [回复]举报

(30+10)*1.25

消防黄河 2022-09-21 10:00 00 [回复]举报

这是对行走距离的要求,是规范明确了的一个指标。若果您要问怎么计算得来的,那是根据人行速度和疏散时间要求等因素综合考虑计算得出的。可多看看规范条文解释。

小黑13218525821 2022-09-23 00:00 00 [回复]举报

室内距安全出口不应大于30米,有自喷加百分25%,实在有困难时,可以布置一个不大于10米的走道。走道有自喷也加25%

30*1.25=37.5+(10*1.25)=50

关闭

关闭

手机APP下载