厂房室内消火栓的设置问题?

问题一:厂房占地面积大于300平方米无都要设置室内消火栓吗?

问题二:厂房总面积3000平方米,被隔成10个300平米的小厂房,部分没有室内室内消火栓,是否每个小厂房都需要增加?

为梦而生 | 2022-08-13 17:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

周家斌 2022-08-13 21:00 00 [回复]举报

刘丽波 2022-08-14 06:51 00 [回复]举报

问题一,除《建规》8.2.2规定的情况,均需要设置消火栓。

问题二,设置消火栓的建筑,要求全保护,保护不到的地方需要增设消火栓。