消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防控制室

消防控制室什么情况下可以设置一个房门

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

Demon Hunter 2022-03-18 15:32 00 [回复]举报

因为工作中遇到过类似问题,所以凑个热闹回答一下。

您所问及的这个问题,在建筑防火规范中没提到,个人觉得可以参考办公用房的相关数据,也就是不大于120平米设置一个疏散门。

另外,对于房间纵深,也就是房间内疏散距离(房间内最远一点到疏散门的距离),可结合消控室所在的建筑高度进行判断,例如在某高层大楼,就按照高层建筑内的用于办公的房间计算疏散距离计算。以上为个人意见,抛砖引玉,大家一起讨论。

石小东 2022-03-18 19:13 00 [回复]举报

《建规》6.2.7 附设在建筑内的消防控制室、灭火设备室、消防水泵房和通风空气调节机房、变配电室等,应采用耐火极限不低于2.00h的防火隔墙和1.50h的楼板与其他部位分隔。     设置在丁、戊类厂房内的通风机房,应采用耐火极限不低于1.00h的防火隔墙和0.50h的楼板与其他部位分隔。     通风、空气调节机房和变配电室开向建筑内的门应采用甲级防火门,消防控制室和其他设备房开向建筑内的门应采用乙级防火门。

8.1.7 设置火灾自动报警系统和需要联动控制消防设备的建筑(群)应设置消防控制室。消防控制室的设置应符合下列规定:     1 单独建造的消防控制室,其耐火等级不应低于二级;      2 附设在建筑内的消防控制室,宜设置在建筑内首层或地下一层,并宜布置在靠外墙部位;     3 不应设置在电磁场干扰较强及其他可能影响消防控制设备正常工作的房间附近;      4 疏散门应直通室外或安全出口

除歌舞娱乐放映游艺场所外,防火分区建筑面积不大于200m2的地下或半地下设备间、防火分区建筑面积不大于50m2且经常停留人数不超过15人的其他地下或半地下建筑(室),可设置1个安全出口或1部疏散楼梯。   

消防控制室如果在地下:5.5安全疏散和避难 除本规范另有规定外,建筑面积不大于200m2的地下或半地下设备间、建筑面积不大于50m2且经常停留人数不超过15人的其他地下或半地下房间,可设置1个疏散门。


关闭

关闭

手机APP下载