请问大家!有252只消防广播,安装多大功率的功放?

川人 | 2022-02-11 15:37
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

半知半解 2022-02-11 17:05 10 [回复]举报

一般每个广播的是不小于3W的(客房内设置专用扬声器除外)。所以你这个252只最少要756W的功放,具体的看你的广播是多大的,而且系统需要预留一定的存量,建议最少安装两个500W的功放

郭子123 2022-02-11 19:16 10 [回复]举报

消防广播大多会采用3w,用现场广播数量乘3w得到总功率,同时需要考虑线损,配置中常用且比较保险的做法是现场广播数量乘4.5w得到总功率去选择功放的大小。