大神们,帮帮忙,排烟问题请教下。

排烟规范中:对于需要设置机械排烟系统的房间,当其建筑面积小于50㎡时,可通过走道排烟,排烟口可设置在疏散走道;排烟量应按本标准第4.6.3条第3款计算。


那请问,如果房间是小于50㎡的酒店,公共走道内设置有机械排烟,防烟分区是否就按走道的计算就好了?  这些小房间内的面积需要纳入计算防烟分区吗?



查规范 | 2021-12-23 10:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

学生 2021-12-23 11:20 00 [回复]举报

防烟分区应该按走道计算;小房间是独立的防烟分区,只是借用走道排烟,不计入走道面积。

查规范   回复: 学生2021-12-23 15:32

谢谢

0    0 [回复]举报

刘丽波 2021-12-23 12:29 00 [回复]举报

本条款仅说排烟口可设于走道,排烟量如何计算,没有说可以与走道排烟口合并以及合并后排烟量如何计算的问题。此条款存在一些争议,各地也出现了一些地标要求。

查规范   回复: 刘丽波2021-12-23 14:46

谢谢刘老师

0    0 [回复]举报

GANSTER 2022-02-10 14:44 10 [回复]举报

看规范条文解释中的“仅于”、“权宜”等字眼,就应该明白这里只要控制好走道排烟就可以了,排烟量计算规范也非常明确不存在歧义,没有必要再去考虑房间情况,但是这个时候的走道就不能考虑是否20米长度限值了,也就是说不论长短都要做。再说了,走道里的烟是从哪儿来的,不就是从房间里溢出的吗,走道的排烟计算已经充分考虑到这一蔓延过程,很多人到现在还在纠结走道+房间面积,对规范的用意没有理解透彻,钻入牛角尖出不来。

查规范   回复: GANSTER2022-02-11 16:16

大神答复让我 顿悟,非常感谢。

0    0 [回复]举报