集中控制应急照明灯具能否采用插头连接

GB53109-2018 4.4.3 应急照明控制器主电源应设置明显的永久性标识,并应直接与消防电源连接,严禁使用电源插头;应急照明控制器与其外接备用电源之间应直接连接。照明灯具是否也需要直接连接。

喆喆 | 2021-10-08 10:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

青衫 2021-10-08 15:06 00 [回复]举报

4.5.5 非集中控制型系统中,自带电源型灯具采用插头连接时,应采用专用工具方可拆卸。那就是集中控制型灯具不能采用插头连接。