消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

甲类中间仓库能否设置在多层或高层厂房当中?

甲类中间仓库能否设置在多层或高层中?如果能够设置,还有像丙类中间仓库的占地面积不超过仓库一个防火分区面积的要求吗?

喷头 | 2021-07-20 14:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

刘丽波 2021-07-20 22:27 00 [回复]举报

我是主修暖通专业的,请咨询建筑专业人士。

消防网友68723 2021-10-09 16:07 10 [回复]举报

 厂房内设置中间仓库时,应符合下列规定:
    1 甲、乙类中间仓库应靠外墙布置,其储量不宜超过1昼夜的需要量;
    甲、乙、丙类中间仓库应采用防火墙和耐火极限不低于1.50h的不燃性楼板与其他部位分隔;
    3 丁、戊类中间仓库应采用耐火极限不低于2.00h的防火隔墙和1.00h的楼板与其他部位分隔;
    4 仓库的耐火等级和面积应符合本规范第3.3.2条和第3.3.3条的规定。

关闭

关闭

手机APP下载