室内灭火器数量配置要求

室内多大面积配置灭火器

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

徐海金 2025-02-10 10:11 00 [回复]举报

按保护面积、保护距离算。单栋的面积小的也要配的

龙行天下的龙 2025-02-10 11:21 00 [回复]举报

建筑灭火器配置设计规范 GB50140-2005 >

6.1.1 一个计算单元内配置的灭火器数量不得少于2具。

6.1.2 每个设置点的灭火器数量不宜多于5具。

6.1.3 当住宅楼每层的公共部位建筑面积超过100㎡时,应配置1具1A的手提式灭火器;每增加100㎡时,增配1具1A的手提式灭火器。

详细计算方式参照规范条文。

赖峰 2025-02-17 16:56 00 [回复]举报

这个需要根据火灾危险性和平面面积计算,参考  《建筑灭火器配置设计规范 GB50140-2005》