氢气探头安装在天花板下,是否需要考虑天花板的横梁对其检测范围的影响?

单位有电池间,考虑到电池是有可能有氢气产生,在电池间的天花板下面安装了氢气探头。但是天花板有横梁,深度超过了0.5m,对这种情况是否需要在横梁另外一侧也要安装上一个氢气探头?如果需要,具体是哪个规范,哪个条款要求的呢?

消防网友84139 | 2024-11-18 15:49
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

jinyanwu 2024-11-19 08:36 00 [回复]举报

根据《火灾自动报警系统设计规范 GB50116-2013》:

根据现场隔断之间面积查附表F和G判断一下即可。