消防软管卷盘对供水压力水源有要求吗?

消防软管卷盘对供水压力水源有要求吗?

依据是哪个规范条文?

李慕白 | 2024-06-05 19:05
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

安洪全 2024-06-06 10:58 10 [回复]举报

仅设卷盘的情况可使用生活给水,增设软盘的应该同室内消火栓的要求


消防给水及消火栓系统技术规范 GB50974-2014

6.1.8 室内应采用高压或临时高压消防给水系统,且不应与生产生活给水系统合用;但当自动喷水灭火系统局部应用系统和仅设有消防软管卷盘或轻便水龙的室内消防给水系统时,可与生产生活给水系统合用。


7.4.2 室内消火栓的配置应符合下列要求:    

1 应采用DN65室内消火栓,并可与消防软管卷盘或轻便水龙设置在同一箱体内;    

2 应配置公称直径65有内衬里的消防水带,长度不宜超过25.0m;消防软管卷盘应配置内径不小于ф19的消防软管,其长度宜为30.0m;轻便水龙应配置公称直径25有内衬里的消防水带,长度宜为30.0m;    

3 宜配置当量喷嘴直径16mm或19mm的消防水枪,但当消火栓设计流量为2.5L/s时宜配置当量喷嘴直径11mm或13mm的消防水枪;消防软管卷盘和轻便水龙应配置当量喷嘴直径6mm的消防水枪。