消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

大车间采用了光束感烟探测器,一个光束感烟跨了好几个防烟分区,该怎么联动排烟口?

有一个超级车间,采用光束感烟,车间内有很多个防烟分区,其中存在一个光束感烟跨两三个防烟分区的情况,这种情况下该怎么联动排烟风口?是同时打开跨所有防烟分区的风口吗?还有是一个光束报警联动还是两个光束同时报警联动?

zhangl28 | 2024-04-16 22:19
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

南明离火 2024-04-17 14:37 00 [回复]举报

红外对射 不应跨越防烟分区,是否是通风图未与报警图校核

一个呆呀 2024-04-18 11:38 00 [回复]举报

就当是点型感烟,每个防烟分区都得有探测器

壹壹 2024-04-18 17:30 00 [回复]举报

根据GB50116-2013 4.5 防烟排烟系统的联动控制设计 4.5.2 排烟系统的联动控制方式应符合以下规定:1 应由同一防烟分区内的两只独立的火灾探测器的报警信号,作为排烟口、排烟窗或排烟阀开启的联动触发信号,并应由消防联动控制器联动控制排烟口、排烟窗或排烟阀的开启,同时停止该防烟分区的空气调节系统。

上述条文已经说的很清楚了,由于火灾联动需求,火灾探测器的设置必须要以防烟分区为界,即哪着火哪报警,哪报警哪联动。

关闭

关闭

手机APP下载