在设置喷淋的前提下,洁净厂房,除了医疗B级洁净室不设置喷淋,是否可以理解为其他洁净室都要设置喷淋?

消防小白XXXX | 2024-01-08 15:46
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

安洪全 2024-01-09 08:52 00 [回复]举报

我觉得您的理解没问题,厂房该设设,核心工艺部位可以不设。


医药工业洁净厂房设计标准 GB50457-2019

10.4.4 当医药工业洁净厂房内设置自动喷水灭火系统时,除应符合现行国家标准《自动喷水灭火系统设计规范》GB 50084的有关规定外,尚应符合下列规定:    

1 当设置自动喷水灭火系统时,宜采用湿式自动喷水系统;    

2 空气洁净度在B级及以上医药洁净室,不宜设置喷头。

条文说明:

10.4.4 医药工业洁净厂房的特点是房间多、走道曲折,当火灾发生时不易及时发现,而湿式自动喷水灭火系统均有反应速度快,可有效扑灭初期火灾,在医药工业洁净厂房设计中得到广泛应用,无不良情况发生。    而对于空气洁净度B级及B级以上的医药洁净室,由于这些区域大多用于无菌药品的生产,洁净室的温度、湿度,悬浮粒子数和微生物限度严格受控,且室内需要定期的清洁消毒。所以对于这些医药洁净室,为防止由于喷淋系统误操作而影响洁净级别,对药品质量造成潜在污染的不利影响,本条提出了对于B级及B级以上的高级别医药洁净室不宜设置喷头的要求。