消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

通用规范中室内消火栓系统设置问题

请问假如有栋旅馆建筑,未达到《建筑防火通用规范》第8.1.7条第5款建筑体积5000立方的要求,但超过15米达到第6款的要求,需要设置室内消火栓系统吗?即第6款中的其他单、多层民用建筑包含第5款的建筑类型吗?谢谢!

我已不是我 | 2024-01-03 15:39
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

安洪全 2024-01-03 16:40 00 [回复]举报

需要设置,条件是“或”的关系

阳明心 2024-01-04 09:20 00 [回复]举报

明确是旅馆建筑,只看第5款。

即第6款的其他单多层民用建筑不包含第5款的建筑类型

我已不是我   回复: 阳明心2024-01-04 11:14

感谢解答!感觉第5款里是相对较危险的场所,要求一般是要高一点。但第5、6款结合起来看的话,在问题中的一些特殊情况下,这类场所要求可能比办公等其他场所还要低了。似乎有点不太合理。

0    0 [回复]举报

关闭

关闭

手机APP下载