消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

大型商业综合体中每一家商铺的喷淋加一个阀门是否合规。

现状:店铺装修消防改造,泄掉一个防火分区的水,增加了风险,浪费了水。

提议:是否可以在每一家商户的消防入户水管上增加一个单独的阀门。

恒隆 | 2023-02-16 11:45
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

周家斌 2023-02-16 12:50 00 [回复]举报

建议加信号阀。

张牙舞爪的张 2023-02-16 20:30 00 [回复]举报

规范没说不可以,就是默认同意。

消防黄河 2023-02-18 08:15 00 [回复]举报

理念很好,但现实如果要做应同时在每户商铺末端设置排气装置,该末端水平管还需正好在区域相对较高位置。不一定容易实现的。否则如何恢复系统?

恒隆   回复: 消防黄河2023-02-18 18:22

排气应该问题不大,用三通加堵头。

0    0 [回复]举报

一路同行 2023-02-18 15:05 00 [回复]举报

规范未做规定应该可以,但阀门应有地址反馈主机

阳明心 2023-03-29 16:27 00 [回复]举报

对,加信号阀应该可以的

关闭

关闭

手机APP下载