关于楼梯间及其前室的机械加压送风的风量计算

高度在33-50米之间的住宅楼设了防烟楼梯间,每层只在前室设了1个机械加压送风口(490mm*480mm),楼梯间前室开向楼梯间的门(1.6*2)㎡,我想问一下各位大佬,这样要达到门洞风速1m/s,风口的风速岂不是远远大于7m/s,是设计错误了吗?那个风口小了吗

消防学徒 | 2022-11-23 19:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

mshm 2023-02-09 17:16 00 [回复]举报

前室风量=走道开向前室的门洞风量+未开启风阀漏风量。与前室进入楼梯间的门没关系。