在很多项目中一直有个问题争议较大,就是幕墙的钢龙骨是否需要按照钢结构做防火涂料,请给予明确做还是不做,有什么具体的依据吧,以便项目上好具体操作,谢谢。

hui | 2021-10-11 12:44
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

窝窝头 2021-10-13 09:47 00 [回复]举报

钢结构的梁柱板这些,是考虑它是建筑承重的一部分,疏散楼梯是考虑人员疏散需要,所以需要考虑耐火极限要满足上表的要求。

幕墙钢龙骨无消防上的需求,不是消防的一部分,不需要做防火涂料。

周家斌 2022-05-10 17:31 00 [回复]举报

不需要,幕墙龙骨不是建筑结构,只要满足装修构件承载要求,《钢结构防火技术规范》 GB51249-2017