消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

200-600mm梁,感烟探测器在3米高度,是每个梁之间都加烟感么?

3702 | 2025-06-04 18:31
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

牛丫头消防课堂 2025-06-05 10:20 00 [回复]举报

不用,你需要依据《火灾自动报警系统设计规范》 GB50116-2013附录G 按梁间区域面积确定一只探测器保护的梁间区域的个数,考虑一个探测器能保护的梁间个数。


关闭

关闭

手机APP下载