消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问水力警铃不持续响是怎么回事?

              有个多层小区,6层屋顶设置了一个消防水箱,12m³,给地下室喷淋和消火栓管网补水。有个地下室设置了喷淋。泵房设置了一组湿式报警阀组。只有大泵没有稳压泵。用大泵启动的时候压力开关动作水力警铃持续响。但是我用泄水阀测试的时候警铃大概响5秒左右再停止15秒左右再响,如此循环,维保单位说是不正常现象,我们看了下过滤网也没堵,延时器管网也正常有水流出,请问这个问题是否正常,需要怎么解决呢?

17 | 2025-05-21 09:28
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

空中 2025-05-21 14:43 00 [回复]举报

水力警铃应持续报警

1.看看警铃管路或铃锤是否有杂物,被卡住

2.本身故障,更换警铃

17   回复: 空中2025-05-21 20:30

警铃管路的水流时有时无,和描述的差不多,所以导致警铃响一会停一会。警铃本身没有卡顿,因为大泵启动会一直响。

0    0 [回复]举报

EHS专家-DL 2025-05-21 14:47 00 [回复]举报

应该不正常,无稳压装置的临时高压系统在低压工况下的稳定性缺陷。可检查延时器下部节流孔板孔径(标准应为3mm),若存在锈蚀或堵塞需更换;确认延时器排水管径不小于DN20且无弯曲压扁现象,确保排水通畅。

17   回复: EHS专家-DL2025-05-21 20:29

你好,我把水力警铃后盖打开观察,发现水流也是一会有一会无的,这个现象说明什么?别人告诉我把节流孔板孔给缩小,这样往延时器的水流就会大,那样警铃就会持续动作,这样对不对?

0    0 [回复]举报

EHS专家-DL   回复: 172025-05-22 10:51

是有一定道理,可以尝试将节流孔板孔径分阶段缩小至2~3mm。或者也检查一下 是否泄水阀是否全开,测试泄水管路是否有堵塞。。。

0    0 [回复]举报

李勤 2025-05-22 10:45 00 [回复]举报

看看报警管路是否正常,有时候警铃附近接口生胶带出来,挡在警铃管道口会有这种现象。在用手动拨一下警铃看是否灵活,是否卡顿

关闭

关闭

手机APP下载