丙类车间设格栅楼板防烟分区怎么划分?

丙类车间内设三层格栅楼板,透空率0.5以上,划分防烟分区是按照一层考虑还是三层?

紫星梦宸 | 2025-02-06 11:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

潘天坤 2025-02-06 11:43 00 [回复]举报

净高是多少米?三层格栅板分别位于几米净高的位置

有遇到过一些洁净厂房项目,用镂空网分为上下区域,此时机械排烟口设置在顶处,下区域无排烟设施。楼主的情况大概率也是属于同一空间,然后下部区域不设置排烟设施。三层区域的话要注意空间净高及排烟量的计算就是了,可能会大于6米

紫星梦宸   回复: 潘天坤2025-02-06 11:49

每7m设一层格栅楼板,总高度21m多了,按照一层空间或者三层空间考虑都感觉不太对劲

0    0 [回复]举报

潘天坤   回复: 紫星梦宸2025-02-06 12:12

三层镂空板不是防烟分隔措施,属于同一空间

此时按21米净高考虑排烟量的设置情况即可

1    0 [回复]举报

赖峰 2025-02-06 11:55 00 [回复]举报

防烟分区的划分与是否设置格栅吊顶无关,防烟分区划分综合考虑车间高度、面积、长边长度相关。

车间防烟分区按照一层考虑。
具体防烟分区划分参考
建筑防烟排烟系统技术标准 GB51251-2017第4.2

PQ 2025-02-06 15:31 00 [回复]举报

根据建规要求,楼板必须达到相应的耐火极限要求,格栅形式无法满足相应的耐火完整性和隔热性要求,因此应该整体作为一个防火分区考虑,防烟分区的划分也应在此基础上进行考虑。