消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

麻将室嵌套在台球厅里,台球厅按走道核对疏散距离的做法,到底可不可行?或者怎么计算稳妥一点?

小唐4563 | 2024-12-25 15:39
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

小唐12321 2024-12-25 16:04 00 [回复]举报

不可行,台球厅算房间内,不是走道。

wetom 2024-12-25 17:25 00 [回复]举报

按大空间疏散不行吗?

云中飞翔 2024-12-26 08:35 00 [回复]举报

如果满足一二级耐火等级,疏散门不少于两个,可以参照:室内任一点至最近疏散门或安全出口的直线距离不应大于30米,当疏散门不能直通室外地面或安全出口时,应采用长度不大于10米的疏散走道通至最近的安全出口。当该场所设置自喷时,两个距离可分别增加25%。如果满足不了,参照歌舞娱乐袋形走道疏散距离要求。

@2017年秋   回复: 云中飞翔2024-12-30 10:00

老师  请教一下  这种情况算不算是经过其他房间才疏散到安全出口呢?

0    0 [回复]举报

云中飞翔   回复: @2017年秋2024-12-31 09:37

这种情况比较普遍,现在大一点的饭店的大厅内都是有包间的,和你们比较类似,

0    0 [回复]举报

小唐4563   回复: 云中飞翔2025-01-09 15:02

老师,这种直接大厅+包间个人觉得属于房间嵌套类,就发的截图里面就相当于把大厅按疏散通道进行考虑,这种就有点争议。所以想确认一下这种疏散计算怎么考虑合适。因为直接把大厅当做疏散通道来计算疏散距离这种存在争议,没有定论。所以想确认下这种场所内的疏散到底怎么计算合适。

目前处理的方式就是把包房门全部取消做成门洞,也就是包房和大厅形成一整个大空间来考虑,这种只能说是取巧,但是实际那种大厅直接就是包间的这种嵌套型的疏散算法还是没解决。

0    0 [回复]举报

云中飞翔   回复: 小唐45632025-01-13 19:53

你说的可行,包房门取消后,可以参照大厅的疏散距离考虑,也就是厅内30米,庭外10米,设自喷,分别增加25%。

0    0 [回复]举报

o夕雾 2024-12-26 10:26 00 [回复]举报

台球厅+棋牌室一起整个按大空间考虑,台球厅和棋牌室内任意一点到楼梯间的距离小于30m

关闭

关闭

手机APP下载