消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于风管穿越防火墙、防火隔墙防火阀两侧2米范围内风管防火包裹问题

关于风管穿越防火墙、防火隔墙防火阀两侧2米范围内风管防火包裹问题,一直没弄清楚建筑上哪些墙体属于防火隔墙,除了风机房、水泵房、防火分区隔墙外还有哪些墙体属于防火隔墙,能否简单理解为隔墙上设置了防火门的就为防火隔墙或者防火墙?楼层上风管出井道部位是防火阀两侧风管耐火极限是否需与风井墙体一致?风井墙体是否为防火隔墙?防火阀靠风井一侧两米防火包裹如何实施?

laifashuai | 2024-12-03 00:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

同同不同 2024-12-03 08:25 00 [回复]举报

凡是设计有耐火极限要求的墙体均为防火墙或防火隔墙,风井墙体耐火极限一般不小于1h,穿墙位置2m内的镀锌钢板风管做法可采用岩棉板、防火卷材等达到一小时耐火极限

laifashuai   回复: 同同不同2024-12-03 16:45

那风井处只能做一侧包裹了。

就是不好区分哪些是防火隔墙,哪些墙体有耐火极限?

0    0 [回复]举报

同同不同   回复: laifashuai2024-12-04 07:01

设计说明会有

0    0 [回复]举报

潘天坤 2024-12-04 14:05 00 [回复]举报

一般来说,有一定耐火极限的墙体就属于防火隔墙,常见为设备房隔墙、疏散走道两侧隔墙、防火分区分隔处、竖井处等(当然普通墙体也有难燃0.5小时的要求但是此区域一般不认为是防火隔墙)

一般有一定耐火极限要求的墙体设置门,需要设置防火门,当然也有存在超额设计的情况,墙体是否属于防火隔墙,还是取决于此处墙体耐火极限

井道一般为1小时候耐火极限,可以认为是防火隔墙,穿越处风管外壁应应设置不低于井道耐火极限要求的防火保护措施,有见过一些做法:例如从井道出来开始做防火包裹,做到防火阀最远边的水平段2米位置,防火阀处开检修口

laifashuai   回复: 潘天坤2024-12-09 12:58

好的,谢谢!!

0    0 [回复]举报

景色浪涛 2025-01-07 14:43 00 [回复]举报

参考建规吧。


看风管穿什么墙就用什么耐火极限的防火包裹。 主要是3小时的防火墙。

关闭

关闭

手机APP下载